brycenesbitt
Senior Member
- Location
- United States
I'm in the EUSERC utility area, which requires a hefty size test bypass meter socket for all multifamily construction.
For anyone else under in EUSERC area, does your local POCO actually require these, and have you found a way to either get a smaller version, or bypass (so to speak) the requirement?
There are several bypass types in the USA that I'm aware of:
This means a new meter stack can't just have a regular meter.
I now have to use something like Eaton 35SS120RAB which is wide and expensive.
And I must say, ugly. Sorry Eaton.
The POCO says that test bypass is required no matter what. I've tried to write to the POCO saying that the common loads are all non-critical: the laundry machines restart the cycle automatically, the security cameras are on battery backup, there are no critical common loads. But so far I just get word back that their hands are tied by EUSERC. Is that true? The POCO will fail a job, and refuse to hook up, unless a TBF is fitted, and of course the job won't plan check.
Is his a holdover from rule of six days.... maybe before disconnects? Or is still a relevant need for the POCO?
For anyone else under in EUSERC area, does your local POCO actually require these, and have you found a way to either get a smaller version, or bypass (so to speak) the requirement?
There are several bypass types in the USA that I'm aware of:
- Horn bypass
- Cotter pin bypass
- Lever bypass
- Test bypass disconnect (also seemingly called TBF)
Which pretty much means all multifamily: I can't think of one that does not have a laundry room or something on the OR list.PG&E Green Book 6.2.2. Test-Bypass Facilities
For single-phase residential installations, test-bypass facilities may be provided, but are not required. However, test-bypass facilities are required for any of the following installations:
NOTE: Single-family homes may be exempt if the elevator system has integrated safety features with a backup battery system acting as an emergency power supply.
- Single-family residential Service Class 320 meter, or residential meter panels that are larger than 225 amp, 120/240 volt, single phase, 3-wire.
- Live-work homes, housing, or buildings.
- Residential meter panels of any size or phase that supply power to elevators.
- All common and tenant area meter panels of any size or phase, at multi-residential and live-work buildings with 2 to 5 units, that supply power to fire alarms or equipment, security alarms, laundry rooms, or significant interior lighting. Significant interior lighting is for hallways, storage rooms or areas, and garage areas.
- All common and tenant area meters at multi-residential and live-work buildings with 6 or more units.
This means a new meter stack can't just have a regular meter.
I now have to use something like Eaton 35SS120RAB which is wide and expensive.
And I must say, ugly. Sorry Eaton.
The POCO says that test bypass is required no matter what. I've tried to write to the POCO saying that the common loads are all non-critical: the laundry machines restart the cycle automatically, the security cameras are on battery backup, there are no critical common loads. But so far I just get word back that their hands are tied by EUSERC. Is that true? The POCO will fail a job, and refuse to hook up, unless a TBF is fitted, and of course the job won't plan check.
Is his a holdover from rule of six days.... maybe before disconnects? Or is still a relevant need for the POCO?