- Chapel Hill, NC
- Retired Electrical Contractor
This was told to me by the NC state chief engineer.
According to the 2017 NEC if you have a car charger that can be wired at different amperages then you must wire the charger at the highest level. For example, the house only has enough power to wire the charger at 240v 20 amps but the charger can be wired to 60 amps. Based on the 2017, he said we would have to wire the unit at 60 amps with #6 wire and a dp 60 breaker. This seems insane. A 20 amp unit being protected at 60 amps.
Now for the 2020 or the 2023 code he said we can wire it at the 20 amp level with a dp 20 breaker and #12 wire.
2023Nec
I get the 2023NEC but does the 2017 interpretation make sense to you? It seems to say what the chief told me but isn't it wrong to put a 20 amp unit on a 60 amp breaker even with the proper wire? We are in transition from the 2017 to the 2023 but it wont be until August before it will happen. The funny thing is we can choose which code to use if we specify on the permit which code we will wire to.
2017
2023Nec
625.42(B) EVSE with Adjustable Settings.
EVSE with restricted access to an ampere adjusting means complying with 750.30(C) shall be permitted. If adjustments have an impact on the rating label, those changes shall be in accordance with manufacturer’s instructions, and the adjusted rating shall appear on the rating label with sufficient durability to withstand the environment involved. EVSEas referenced shall be permitted to have ampere ratings that are equal to the adjusted current setting.
750.30(C)(3) Settings.
Adjustable settings shall be permitted if access to the settings is accomplished by at least one of the following:
- (1)Located behind removable and sealable covers over the adjustment means
- (2)Located behind a cover or door that requires the use of a tool to open
- (3)Located behind locked doors accessible only to qualified personnel
- (4)Password protected with password accessible only to qualified personnel
- (5)Software that has password protected access to the adjusting means accessible to qualified personnel only
2017
625.41 Overcurrent Protection.
Overcurrent protection for feeders and branch circuits supplying equipment shall be sized for continuous duty and shall have a rating of not less than 125 percent of the maximum load of the equipment. Where noncontinuous loads are supplied from the same feeder, the overcurrent device shall have a rating of not less than the sum of the noncontinuous loads plus 125 percent of the continuous loads.