I have a code question on EV Chargers and Non-coincident loads.
There is a subpanel in a non-dwelling detached garage. It’s fed by 3 AWG on an 80 amp breaker. Other than some lights and receptacles, the subpanel's main load is a Tesla Gen2 Supercharger on a 70 amp breaker, which will run a continuous load of 56 amps (80%) when charging.
I want to install a 7500 Watt heater on the same panel (40 amp breaker / 31.25 amp expected load).
The heater and supercharger will not be used at the same time. (Obviously, this would exceed the max load.)
Can I consider the EV Charger and heater a Non-coincident load under 220.60?
Unlike a heater and A/C, someone could attempt to run both at the same time.
There is a subpanel in a non-dwelling detached garage. It’s fed by 3 AWG on an 80 amp breaker. Other than some lights and receptacles, the subpanel's main load is a Tesla Gen2 Supercharger on a 70 amp breaker, which will run a continuous load of 56 amps (80%) when charging.
I want to install a 7500 Watt heater on the same panel (40 amp breaker / 31.25 amp expected load).
The heater and supercharger will not be used at the same time. (Obviously, this would exceed the max load.)
Can I consider the EV Charger and heater a Non-coincident load under 220.60?
Unlike a heater and A/C, someone could attempt to run both at the same time.