Ken_S

Senior Member
Location
NJ
Occupation
Electrician
NJ has a code assistance unit within the department that regulates the Uniform Construction Code, they produce a newsletter periodically, the recent edition had an article regarding the size of NM cable permitted for a 48-amp EV charger.

Let me know your thoughts on this, as my understanding on this does not align with what is being permitted.

"One of the more frequent questions we get in the Code Assistance Unit relates to the use of Non-metallic sheath (NM) cable for EV chargers. Specifically, the use of #6 CU on a 48-amp load.

There appears to be a significant portion of code officials with a difference in opinions on how we should apply the requirements found in Article 625 of the National Electrical Code (NEC), with continuous load designation and NM cable.

First let’s start with Article 625; Article 625.41 requires the overcurrent protection device (OCPD) to be sized for “continuous duty,” thus applying a factor of 125% to the full load of the equipment. “Continuous Duty” is a term used to alert installers that considerations must be made to help dissipate excessive heat when a substantially constant load is present for an indefinitely long period of time. This increase is a “cushion” to help the circuit components deal with this heat. There is NO additional current on this circuit.

Article 625.42, however, states: “Electric vehicle charging loads shall be considered to be continuous loads for the purpose of this article." A review of the Code Making Panel notes shows their primary intent is that this continuous load designation is limited to this article and shall not extend to service calculations (Review 220.83. There is no 125% factor for continuous load).

Neither article requires the conductors to adhere to this increase. This may be because the “continuous load” or “continuous duty” designation is intended for the protection of devices and not conductors. Exception #1 to Article 210.19A(1), appears to support this, but because Article 625.41 explicitly requires us to apply the 125% factor, this exception cannot be applied.

So, let’s assume for the sake of this article that we interpret the code to read that the conditions for continuous loads apply to the conductors as well. Table 310.16 of the 2020 NEC shows 6 AWG having an ampacity of 55 amps at 60°C (See 334.80 for ampacity limitations). "Ampacity," as defined by the NEC, is “The maximum current, in amperes, that a conductor can carry continuously under the conditions of use without exceeding its temperature rating.” Based upon table #6, NM can safely carry 55 amps WITHOUT exceeding the temperature rating of the conductor at 60°C. Considering most devices and OCPD’s have dual rated lugs with temperature limitations of 60°C/75°C, limiting the ampacity to 55 amps or less will inherently limit the temperature of any device to be well within its listed operating temperature. Which means, applying the 125% to a conductor which is already limited by 60°C does nothing more to protect the equipment or the conductors in the circuit.

In the 2020 NEC, a change to Article 334.80 was made from “allowable ampacity” to just “ampacity." This change seems to imply that the ampacity safely carried by NM cable is dictated by the actual load and not OCPD. Furthermore, the provisions of Article 240.4 for applications under 800 amps do not exclude NM cable.

Therefore, the opinion of the Code Assistance Unit is that #6 NM cable should be permitted to be utilized for EV chargers with loads not exceeding 48 amps"
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Therefore, the opinion of the Code Assistance Unit is that #6 NM cable should be permitted to be utilized for EV chargers with loads not exceeding 48 amps
Would that logic apply to all such load levels, or only EV chargers?
 

Ken_S

Senior Member
Location
NJ
Occupation
Electrician
If the NEC says that you need a 60 amp conductor (48*125%) I don't see how a 55 amp conductor is ever going to be code compliant.
I completely agree.
That's why I posted the CCC article for input
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
It would be my view that they are are simply incorrect and do not fully understand the NEC requirements for conductor sizing.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I don't have the NEC in front of me but does Article 625 state that the conductors must be sized at 125% like it does for things like water heaters?
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
IMHO the CCC interpretation does not match common reading of the code, but I believe it matches what code _should_ say. (It violates 'Charlie's law'.)

My understanding of the basis of the '125% factor' is that the OCPD must be sized a minimum of 125% of a continuous load in order to ensure proper operation and life of the OCPD. _Then_ the conductors must be increased in size as well in order to ensure that the OCPD properly protects the conductors. The basis for understanding the 125% factor as being OCPD based is the exception that permits '100% rated breakers' to avoid the 125% requirement.

We then combine this with the 'round up rule' where the next larger OCPD may be used to protect a conductor, as long as the ampacity of the conductor exceeds the requirements of the load.

IMHO it would be perfectly reasonable and safe for a 60A to protect a 55A conductor supplying a 48A continuous load. But to be perfectly clear that is _not_ what the code actually says, at least as most people read it. If the NJ CCC shifts the conventional interpretation of the code, or pushes a proper code change, then great.

-Jon
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
If one takes the point of view that an EVSE is not a continuous load, then the conclusion in the OP is correct. 625.41 requires a 60A OCPD, but 210.19(A)(1)(a) only requires 48A ampacity conductors. 240.4(B) requires a minimum of 51A ampacity conductors for the 60A OCPD, and NM #6 has the requisite ampacity of 55A.

But come on, an EVSE is certainly a continuous load. There are EVs out there that will take 48A for 3 hours if plugged in at a low state of charge. Therefore 210.19(A)(1)(a) requires conductors with 60A ampacity.

However, 210.19(A)(1)(a) errs in that requirement. Since ampacity is a continuous rating, there is no need to upsize the conductor itself by 125%. All that is necessary is to ensure the conductor is large enough to carry the load and be protected by the requisite OCPD size, and a 55A ampacity conductor may be protected at 60A per 240.4(B). In other words, all 210.19(A)(1)(a) is doing is preventing the use of 240.4(B) in this situation.

Because of this, I submitted a 2026 PI to add a second exception to 210.19(A)(1) covering this scenario to allow the use of 240.4(B). See https://forums.mikeholt.com/threads/pi-210-19-a-number-two.2573390/

Cheers, Wayne
 