EV Charger Disconnect - 625.43

Status
Not open for further replies.
I am getting more and more jobs to install DC Fast Chargers. These take 480V and or are 240V but at 100 amps.

The code seems pretty clear that a disconnect is required for chargers at 60 amps or larger. However, it seems crazy to put a disconnect in a consumer parking lot that can be accessed by anyone. It also seems to pointless to put a disconnect in some sort of locked enclosure.

What is happening in the real world? Are people putting these disconnects in? I don't see any sort of disconnects out by the Tesla Superchargers. Is this a code section that's not being enforced?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I am getting more and more jobs to install DC Fast Chargers. These take 480V and or are 240V but at 100 amps.

The code seems pretty clear that a disconnect is required for chargers at 60 amps or larger. However, it seems crazy to put a disconnect in a consumer parking lot that can be accessed by anyone. It also seems to pointless to put a disconnect in some sort of locked enclosure.

What is happening in the real world? Are people putting these disconnects in? I don't see any sort of disconnects out by the Tesla Superchargers. Is this a code section that's not being enforced?
If it is out where somebody might open it as a prank, put a padlock on it and lock it closed.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
625.43 does not regulate the location of the required disconnecting means. So you can put it anywhere, and even use a permanent breaker lock on the branch circuit breaker, if those are available for the size of breaker supplying the DCFC.

Cheers, Wayne
 