ElecBolt12

Member
Location
Nj
Occupation
Electrican
It is an existing house with a 200amp panel and the inspector wants a load calculation because we are adding a EV charger. How would you do something like this?
Will be running six gauge wire on a 50 amp breaker to 240V outlet. I assume he wants to see if the panel can hold the extra load. What would be the steps to complete this load calculation?
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
It is an existing house with a 200amp panel and the inspector wants a load calculation because we are adding a EV charger. How would you do something like this?
Will be running six gauge wire on a 50 amp breaker to 240V outlet. I assume he wants to see if the panel can hold the extra load. What would be the steps to complete this load calculation?
You need to do an Article 220 calc.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Tip #1 use the alternate calculation
Tip #2 see the examples in the annex
Tip #3 take pictures of nameplates for HVAC, Dryer, range, etc
 

ElecBolt12

Member
Location
Nj
Occupation
Electrican
What is the alternate calc?
I know the serivce load calc. Like wouldn’t just add the EV charger into the service load calc ex:9.6kw
For a total load of the service?
 

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
There are two different residential calculation methods -- Standard and Optional. The Optional usually comes in with a lower number. Once you've gone over 10KW, most new things add 40% of their nameplate to the load calc. So a 10KW car charger would add 4KW (or about 17amps) to the load calc.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
What is the alternate calc?
I know the serivce load calc. Like wouldn’t just add the EV charger into the service load calc ex:9.6kw
For a total load of the service?
There is "A Pocket Guide to All-Electric Retrofits of Single-Family Homes" with some interesting ways to avoid service upgrades with clever load calcs.

The NEC requires twice as much power allocated to separate appliances, such as oven and range (19,200W) vs combined range and oven (9,600W). Similarly, attaching a microwave oven to the wall triggers an extra, dedicated circuit vs just placing the microwave on the countertop or doghouse cabinet.

Power-sharing car chargers can eliminate service upgrades, by sharing a circuit with similar electric appliances. Car charging automatically resumes when the other appliance is finished.

Circuit-sharing plugs (e.g. NeoCharge, Dryer Buddy, SplitVolt, or hard wired SimpleSwitch) allow one existing high voltage (240V) outlet to power both a car charger and a laundry dryer, or a water heater and a range.

Manual transfer switches can also be installed next to the main fuse box.
 

ESolar

Senior Member
Location
Eureka, CA Humboldt County
Occupation
Electrician/Contractor
There is "A Pocket Guide to All-Electric Retrofits of Single-Family Homes" with some interesting ways to avoid service upgrades with clever load calcs.

The NEC requires twice as much power allocated to separate appliances, such as oven and range (19,200W) vs combined range and oven (9,600W). Similarly, attaching a microwave oven to the wall triggers an extra, dedicated circuit vs just placing the microwave on the countertop or doghouse cabinet.

Power-sharing car chargers can eliminate service upgrades, by sharing a circuit with similar electric appliances. Car charging automatically resumes when the other appliance is finished.

Circuit-sharing plugs (e.g. NeoCharge, Dryer Buddy, SplitVolt, or hard wired SimpleSwitch) allow one existing high voltage (240V) outlet to power both a car charger and a laundry dryer, or a water heater and a range.

Manual transfer switches can also be installed next to the main fuse box.
Where in the NEC does it say that a transfer switch can be used to eliminate one of the loads on the switch from the load calc? (e.g., EV/Dryer transfer switch)
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
Where in the NEC does it say that a transfer switch can be used to eliminate one of the loads on the switch from the load calc? (e.g., EV/Dryer transfer switch)
Grasshopper must learn more code jargon

Try the key phrase:

"Where the circuitry is interlocked"
 

Amps

Electrical Contractor
Location
New Jersey
Occupation
Electrical, Security, Networks and Everything Else.
Tip #1 use the alternate calculation
Tip #2 see the examples in the annex
Tip #3 take pictures of nameplates for HVAC, Dryer, range, etc
#4 Charge the customer for the load calculation work.
 