Hi all. I recently received this panel schedule to review. I'm having trouble understanding how/why the total connected load came out to 72.7kVA.
For referene, the 20A/1P breaker is a 6A 120V load, and the 60A/2P breaker is a 48A 208V load.
According to my math:
(6A *120V) = 720VA
(48A * 208V) = 9,984 VA
(720VA + 9,984VA) * (6 chargers) = 64.2 kVA
This was an explanation I got:
I would greatly appreciate it if someone can tell me what i'm missing here.
Thank you!
For referene, the 20A/1P breaker is a 6A 120V load, and the 60A/2P breaker is a 48A 208V load.
According to my math:
(6A *120V) = 720VA
(48A * 208V) = 9,984 VA
(720VA + 9,984VA) * (6 chargers) = 64.2 kVA
This was an explanation I got:
I would greatly appreciate it if someone can tell me what i'm missing here.
Thank you!