Please see attached sketches. I have 1600A switchboard 277/480V 1600A with main of 1600A. Have 300A breakers which feed power cabinets 150kW. The power cabinets then feed from DC dispensers EV charger.
The switchboard is in concrete pad outside. The sketch shows floor plan of switchboard and the power cabinets. Distance between is 4 feet
The dispensers are on parking lot.
Questions:
1. Nec 2017 section 625.43 requires disconnect. So both the power unit cabinets and the dispensers require disconnect? Or one of them or none of them?
2. Nec 2017 section 625.44(b) requires receptacles. It just says equipment does this mean dispensers and power units require receptacles?
3. Nec 2017 section 625.40 require outlet. I looked at definition of outlet but am confused does this mean each dispensers require receptacle or not?
4. Does the dispensers EV chargers have to be grounded with ground rods? Where is it in NEC 2017?
The switchboard is in concrete pad outside. The sketch shows floor plan of switchboard and the power cabinets. Distance between is 4 feet
The dispensers are on parking lot.
Questions:
1. Nec 2017 section 625.43 requires disconnect. So both the power unit cabinets and the dispensers require disconnect? Or one of them or none of them?
2. Nec 2017 section 625.44(b) requires receptacles. It just says equipment does this mean dispensers and power units require receptacles?
3. Nec 2017 section 625.40 require outlet. I looked at definition of outlet but am confused does this mean each dispensers require receptacle or not?
4. Does the dispensers EV chargers have to be grounded with ground rods? Where is it in NEC 2017?