EV Charger question

olly

Senior Member
Location
Berthoud, Colorado
Occupation
Master Electrician
I don't do a lot of EV chargers installs
I am helping my brother in-law install a charger for his new Ford Lightning. SHM. I am only helping because he is family and I really don’t have time for this, one of those annoying situations that's not paid. The charger is the: Ford Charge Station Pro - 80 AMP WALL BOX



  1. Is an 80A breaker good? Or should it be sized at 125% for continuous duty?.
  2. He has Siemens type QAF2. Do these breakers have adjustment on them?
  3. Would you install GFCI if it were in your garage? Is that to Taboo for this site?
  4. Spec calls for #3 CU. Its going in FNMC, 1” so I will be using THHN. #4 THHN seems fine to me based on code
Before you report me for a DYI look at my history. This just isn't in my wheel house.
Thanks in advance for reading and any reply's given
 

SSDriver

Senior Member
Location
California
Occupation
Electrician
You need a 100 amp breaker, and wire sized for 100A circuit loaded to 80 amps, so #3. Plus you must follow the instructuon manual and it also states #3. So you will.need 1 1/4" conduit. Gfci is not required.

He decided to go "green" hahahhahahahaha. He must pay for it to be hooked up properly.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
He decided to go "green" hahahhahahahaha. He must pay for it to be hooked up properly.
Compared to the gasoline equivalent, yes the F-150 Lightning will generate less pollution over its lifetime. [The impacts will be different, so that requires a judgement as to the tradeoffs involved, but is a pretty safe call assuming the truck doesn't suffer an infant death through collision, etc.]

And yes, you currently pay a premium for that. Most likely the net subsidies are still biased towards the gasoline F-150, but even if not, the electric vehicle market is still maturing, so that's not unexpected.

Cheers, Wayne
 

letgomywago

Senior Member
Location
Washington state
Occupation
residential electrician
Just hooked up one of these. No neutral is needed. Don't worry about gfi it's over 50 amps 1 phase. Copper only and it's 75° at 3 awg so double check your liquid tight. There's a wierd kick on the charger too you can't come in straight up or down.
 

retirede

Senior Member
Location
Illinois
Also….there is a hardware setting that can deprecate the charge rate to 64, 48, 40, or 32 Amps. You are allowed to size the branch circuit based on that setting.
 

letgomywago

Senior Member
Location
Washington state
Occupation
residential electrician
Or he likes the 0-60 time. And/or the using the truck as back-up power for the house.
That backup for the house is a big deal to set up and doesn't come with the charger. Ford has a transfer switch that from what I've seen isn't even available unless that's recently changed. They just only in the past few months got the first orders out.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
That backup for the house is a big deal to set up and doesn't come with the charger. Ford has a transfer switch that from what I've seen isn't even available unless that's recently changed. They just only in the past few months got the first orders out.
Yup. Although it can also be used as a portable generator with an inlet and manual transfer setup, without all that.
 

retirede

Senior Member
Location
Illinois
That backup for the house is a big deal to set up and doesn't come with the charger. Ford has a transfer switch that from what I've seen isn't even available unless that's recently changed. They just only in the past few months got the first orders out.

It is available, but it’s expensive and a PITA to install and get running.
If you have nat gas, it costs less to install a 22 KW generator. Plus, your truck doesn’t have to be home for backup to happen.
 

FionaZuppa

Senior Member
Location
AZ
Occupation
Part Time Electrician (semi retired, old) - EE retired.
You need a 100 amp breaker, and wire sized for 100A circuit loaded to 80 amps, so #3. Plus you must follow the instructuon manual and it also states #3. So you will.need 1 1/4" conduit. Gfci is not required.

He decided to go "green" hahahhahahahaha. He must pay for it to be hooked up properly.
Perfect opportunity to sell the hook-up as a payment service, charging interest along the way. ;)
 

FionaZuppa

Senior Member
Location
AZ
Occupation
Part Time Electrician (semi retired, old) - EE retired.
0-60 in 4 seconds is not to be ignored!
It's also a super waste of resources.
You know eV's burn through tires way faster, yes? Hmmm, where's all that rubber coming from, and where's all that old tire rubber going?
 
Top