sducato
New User
- Location
- Northern California
- Occupation
- Foreman/estimator
I have a customer who wants to put a 30KW 480 volt Bus Charger on a 208 volt circuit. How would I size the step-up transformer?
Greater than 30 kVA? Are you assuming that 30 kW is an output rating, and the charger's input rating will be slightly higher?Welcome to the forum.
208 delta to 480/277 wye, greater than 30kva.
I have a customer who wants to put a 30KW 480 volt Bus Charger on a 208 volt circuit. How would I size the step-up transformer?
Isn't a transformer's rating a continuous rating? That would mean there's no need to use a 125% factor when sizing the transformer.Another reason why I chose 0.8 is because car, bus or truck chargers are considered continuous loads.
Isn't a transformer's rating a continuous rating? That would mean there's no need to use a 125% factor when sizing the transformer.
Cheers, Wayne
I assumed it was the output rating.Greater than 30 kVA? Are you assuming that 30 kW is an output rating, and the charger's input rating will be slightly higher?
Cheers, Wayne
Probably high enough to be negligible, compared to internal losses.I would think the power factor for battery charging would be really high.