Was it 2020 code that implemented GFCI breakers on EV charger receptacles in a residential garage or was it in before that?
 
First required in the 2020 for the receptacle. 625.54
Seems like the chargers themselves have a GFCI function built into them also.
 
First required in the 2020 for the receptacle. 625.54
Seems like the chargers themselves have a GFCI function built into them also.

The charger I just installed had no neural wire

Also a charger is not a receptacle


Sent from my iPhone using Tapatalk
 
I would avoid putting in receptacle outlets for chargers, stay with the ones that can be hard wired.
 
I just looked at a EV installation at a dwelling. 240 volt 50 AMP Unit. Charger can be hard wired or plug. Installation will have to comply with 2020 NEC.

  • If I hard wire the charger in the garage then GFCI protection not required. 210.8 A (2) states "Receptacles" in Garage. NOT OUTLETS. Also 625.54 again states " Receptacles ".
  • If I put charger outside then I have to comply with 210.8 F which states " Outlets ". Then it has to be GFCI protected.
Please Comment
 
I just looked at a EV installation at a dwelling. 240 volt 50 AMP Unit. Charger can be hard wired or plug. Installation will have to comply with 2020 NEC.

  • If I hard wire the charger in the garage then GFCI protection not required. 210.8 A (2) states "Receptacles" in Garage. NOT OUTLETS. Also 625.54 again states " Receptacles ".
  • If I put charger outside then I have to comply with 210.8 F which states " Outlets ". Then it has to be GFCI protected.
Please Comment

A 50A unit would require a 60A branch circuit, which according to 625.44 requires hard-wiring, receptacle is not allowed. GFCI is only required 50A or less (210.8(F)), so 60A hard-wired outdoors would not require GFCI.

That’s how I interpret things….
 
THANK YOU. You made me read the rest of the paragraph. Now I see that up to 50 AMPS for GFCI protection. So 60 AMP outlet would not require GFCI protection (210.8(F))
 
THANK YOU. You made me read the rest of the paragraph. Now I see that up to 50 AMPS for GFCI protection. So 60 AMP outlet would not require GFCI protection (210.8(F))

I got to thinking more about this. I’ve never seen a 50A EVSE. They’re normally 48A for a 60A circuit. If it’s truly 50, a 60A circuit is not sufficient - 50 x 1.25 = 62.5.
 