EV Charger

nizak

Senior Member
I’m sure this has been discussed here before but would like clarification.

I’m installing a Tesla Gen3 charger in a residence.

Product sheet shows 60 amp breaker and lists maximum output at 48 amps.

The 60 amp circuit satisfies the 125% requirements for continuous duty.

#6 NM cable @60deg allows 55 amps. Next size up circuit breaker is 60 amp.

Is the #6 NM cable code compliant to use in this application? If not, why.

This is a single charger with no other loads associated with the dedicated circuit.

Thanks
 

goldstar

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
From my recollection I believe 6/2 MC is the correct cable to use for this EV charger. You'll have to refer to the Tesla specs as well. I don't believe this unit requires a neutral.
 

nizak

Senior Member
No, NM is not compliant. The wire must have an ampacity of 125% of the continuous load (48A), so in this case, 60A.

I agree, no neutral for this and most EV chargers.
So the ampacity rating of 60amps trumps the next size up circuit breaker exception?
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
And I would say the NEC rules are overly conservative in this case. If 60C #6 Cu with a 55A non-continuous load can be protected safely at 60A, why can't the same conductor with a 48A continuous load be so protected? The wire itself is good for 55A continuous, it's just the OCPD that is the weak link, as well as whether the OCPD protects the wire.

Basically 215.2(A)(1)(a) and 210.19(A)(1)(a) should be deleted. Then 215.3 / 210.20(A), along with 240.4, will give almost the same results, with the exception that 240.4(D) can be used in the above situation.

Cheers, Wayne
 

Alexis

Member
Location
Los Angeles
If I may bring this topic again.

I belive 6/2 wouldn't be compliant, singe whine neutral wire cannot be reindentified. Only 4awg and largen can. Would I be connect in this? Hate to waste copper, but the only right way here would be 6/3
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
I belive 6/2 wouldn't be compliant, singe whine neutral wire cannot be reindentified. Only 4awg and largen can. Would I be connect in this? Hate to waste copper, but the only right way here would be 6/3
That is not what NEC 200.7(C)(1) says. You can reidentify the white wire of a cable assembly in any size.

Reidentifying individual conductors pulled in conduit is what is restricted by size.

Cheers, Wayne
 

TwistLock

Member
Location
California
Occupation
Electrician
Then is #6 NM with 60 A breaker allowed as long as you set 55amp max (or lower) in EVSE installer app and place a label next to breaker ?
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Then is #6 NM with 60 A breaker allowed as long as you set 55amp max (or lower) in EVSE installer app and place a label next to breaker ?
55 amps needs to be the calculation after adding the 125% continuous factor. So if you can tell the EVSE that the breaker is 55A, or tell it to allow max 44A or lower actual max current, then yes, it's allowed.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
The last Tesla I installed required by MFG instruction an insulated Grounding conductor that in of itself would prohibit the use of NM. I ran a conduit sized to allow for a neutral to be added if needed. But I believe you can run 6/2 MC as it has an insulated grounding conductor and the neutral being a cable assembly can be reidentified.
 