Certainly that is the meaning of the text in 220.84.Can the demand factor shown on table 220.8 be used for Electrical Vehicle Chargers if they are being fed from the dwelling panels?
...
To summarize:
I think that the way 220.80 / 220.40 are written excludes special equipment as being included in the demand factors.
...
?Would there be anything wrong with considering the EV chargers in a bank of them to be continuous loads and sizing the wiring and OCP to the worst case condition, which would be all of them running as such at full capacity at the same time?
Yes, I mean if the service is much larger than than all the loads combined. Sorry that I diverted the question.?
You mean if that were a larger service size than the 220.84 required calc?
Note the OP said the EVSEs would be fed from the dwelling panels so I don't know why we'd be talking about a 'bank' or group of EVSEs.
Would there be anything wrong with considering the EV chargers in a bank of them to be continuous loads and sizing the wiring and OCP to the worst case condition, which would be all of them running as such at full capacity at the same time?
Thanks. I had to design a couple of banks like this, and it being somewhat out of my wheelhouse I wanted to be conservative.If I understanding your question, then no. There is nothing wrong with oversizing the circuits that feed the EV charger(s). Nor is there anything wrong with overestimating their effects.
Utilities have a lot of data on demand versus connected. Plus, they have no problem overloading their transformers because data shows it is cheaper for them to shorten the life of the transformer for limited over load conditions versus the cost of installing one that is lightly loaded most of the time.When your all driving around take a look at what size transformers utilities install, its amusing, I was at a place that had a 17 unit complex, 17 100A services grouped in meter packs, plus a 200A house panel that served a laundry room, I think the utility transformer was a 50kVA.