Building department down here in South Florida is giving me an issue for including an EV charger in my load calculation (using optional method 220.83) under the fixed appliance section and told i cant use the demand factor and have to include the full load @100%. I Call Bull Spit!! See plan review comment....
EV charger is considered a continuous load as per NEC 625.42EV charger load needs to be calculated at 100% and not part of the demand reduction.
This is for branch circuit load not feeder! I even included the extra 25% in the calculation bringing the EV charger from 9600 KV to 12000 KV before adding the Load Factor. PS I use the Mike Hold Residential Load Calc on the app, its awesome!! I am posting this it is because it does make a difference whether the customer can have a charger installed legally or not with his current service.
EV charger is considered a continuous load as per NEC 625.42EV charger load needs to be calculated at 100% and not part of the demand reduction.
This is for branch circuit load not feeder! I even included the extra 25% in the calculation bringing the EV charger from 9600 KV to 12000 KV before adding the Load Factor. PS I use the Mike Hold Residential Load Calc on the app, its awesome!! I am posting this it is because it does make a difference whether the customer can have a charger installed legally or not with his current service.