Ev chargers code violation

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Attached sketch shows 480/277V three phase switchboard with 1600A main breaker. The switchboard feeder breaker 300A feed 150kW power cabinet. The power cabinet convert ac to dc then feed 150kw dispenser 400V dc to 927dc.

The switchboard breakers when I look at submittal is 4 poles. Neutral also has breaker

Anyone who has done this sort of work is this usual? Is 4 pole breaker code violation or is their any exceptions?

512841ba068bcbb257f2baf65d93d0fc.jpg
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
You sure it’s not just a quad breaker for that 150kW load?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I have a feeling this is something done in Europe by someone who does not understand US electrical systems.
I looked at the manufacturer's site but found little info on "listing" other than C-E which may help explain things.
 

jap

Senior Member
Occupation
Electrician
Am I not reading the print correctly? The drawing specifies MCCB 3P, but the spec shows MCCB 4P.

I agree it's a confusing line diagram.

Only 3 of the 4 poles shown on the MCCB are drawn as a common trip ,and,the overcurrent protection devices to Ev Quick chargers 1 and 2
are not drawn as common trip at all in my world.

JAP>
 