hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I am really stuck on this would really appreciate all your help. Previous post dealt with issues of 625.43. However this post its about protecting DC conductor between dispensers and power cabinet. The designer tells me the power cabinets have no internal breaker. Only software that detects 350A above and stops the system. Also designer says power cabinet each module has 20A 24 fuses in parallel which would protect DC cable 2 sets of 350kcmil. I have never heard if this but not sure
Attached sketches I have 480/277V 1600A switchboard. The switchboard 300A AC feeder breaker feeds 175kw(150kw) power cabinet. The power cabinet feeds the dispensers.
Power cabinet is Signet High Power Charging Model HpC175K.
From the power cabinet to the dispensers there are 2 sets if 2#350kcmil AL +#2 Gnd DC conductors
The power cabinet has 8 modules. Each module has 24 20A fuses in parallel. Their are no breaker or fuses other than those.
Questions:
1. Would not the 2 sets of 350kcmil AL DC conductors need to be protected? If so then would not one require overcurrent protection or would 24 20A fuses in parallel in each module be ok and would be acceptable to protect the cable?
2. Has anyone encounter the EV chargers below and has anyone placed overcurrent protection between the dispensers and the power cabinet? If yes then where is it in NEC 2017 section 625?
Attached sketches I have 480/277V 1600A switchboard. The switchboard 300A AC feeder breaker feeds 175kw(150kw) power cabinet. The power cabinet feeds the dispensers.
Power cabinet is Signet High Power Charging Model HpC175K.
From the power cabinet to the dispensers there are 2 sets if 2#350kcmil AL +#2 Gnd DC conductors
The power cabinet has 8 modules. Each module has 24 20A fuses in parallel. Their are no breaker or fuses other than those.
Questions:
1. Would not the 2 sets of 350kcmil AL DC conductors need to be protected? If so then would not one require overcurrent protection or would 24 20A fuses in parallel in each module be ok and would be acceptable to protect the cable?
2. Has anyone encounter the EV chargers below and has anyone placed overcurrent protection between the dispensers and the power cabinet? If yes then where is it in NEC 2017 section 625?