See attached sketch, I have 277/480V, three phase, 2000A switchboard. Have 600A feeder breaker feeding the power unit which concert AC to DC. The power init then feeds the dispenser unit both separate.
I also have from the switchboard 30A 120V single phase breaker which feeds the dispenser auxiliary power for heat exchanger, payment system and display module.
NEC 2017 section 625.43 talks about disconnecting means. I have two of them that feed the dispenser would both be required to be lockable open? Can switchboard feeder breakers act as that disconnecting means both the dispenser and the power unit are within sight 30 feet away? Would 30A breaker fall under NEC 2017 section 625.43 or not?
I also have from the switchboard 30A 120V single phase breaker which feeds the dispenser auxiliary power for heat exchanger, payment system and display module.
NEC 2017 section 625.43 talks about disconnecting means. I have two of them that feed the dispenser would both be required to be lockable open? Can switchboard feeder breakers act as that disconnecting means both the dispenser and the power unit are within sight 30 feet away? Would 30A breaker fall under NEC 2017 section 625.43 or not?