[210.8(A)(2)] Garage requires all 125 -V, 1ph 15 & 20A receptacles to have GFCI protection...etc. 2008 cycle. Article 625 does not seem to have an exception to the 210.8 requirement when EV Charger stations have included a GFCI function to the 125V interface. Would an ROP submission such as stating the above for substantiation be acceptable for including an exception as follows:
(210.8(A)(2) Exception)
Recommendation: Add Exception to (2): "Receptacles that have GFCI protection integral with EV Charger Station equipment and are supplied from a dedicated branch circuit without a GFCI protection shall be permitted."
Any comments would be appreciated.
(210.8(A)(2) Exception)
Recommendation: Add Exception to (2): "Receptacles that have GFCI protection integral with EV Charger Station equipment and are supplied from a dedicated branch circuit without a GFCI protection shall be permitted."
Any comments would be appreciated.