Yes, maybe, but what Code cycle?
I currently out of town for a couple days and do not have my code book with me. Does the code have any special requirements for a EV charger in a house?
Do not know the details at this point, but I believe it would be 240 volt/50amp
“ shoot low boys their riding shetland ponies”
Aren't you required to add GFCI protection? NEC 2020 Article 625.54If it’s to be cord and plug connected, you just wire a 14-50 receptacle in a compliant manner.
Not sure how 2020 reads but 2017 reads as only 150V to ground or less and 50A or less requires GFCI.Aren't you required to add GFCI protection? NEC 2020 Article 625.54
625.54 was added to the 2017 NEC as a TIA, I believe, and requires the GFCI for EVSE receptacles, independent of location.Depending on location, likely yes. That’s part of “in a compliant manner.”
OP did state 2017 code.
Cheers, Wayne
That's true for the 2017 NEC only if your jurisdiction hasn't adopted the TIA. Not sure how TIA adoption works.The charger controller has it built in, so unless you are on 2020, you are not required to for the 30 and above charger receptacle.
Cheers, Wayne
EVSEs have always been required to have a "a listed system of protection against electric shock of personnel" (625.22) which is some form of GFP, I believe, not necessarily 5 ma trip threshold.Not all EVSEs have built in GFCI.
The 2017 TIA is not an extra option, it's an extra requirement. So if you are subject to the TIA, you must GFCI protect the receptacle intended for the cord and plug connected EVSE. If you are under the 2017 without the TIA, then the receptacle is only subject to the usual requirements in Article 210.and you’re allowed to use the TIA
All of the commercial ones I have installed have it, haven’t done many residential ones, so I don’t know about them.Not all EVSEs have built in GFCI. So if your current one does, and you’re allowed to use the TIA, you don’t GFCI the receptacle. Owner decides to get a different EVSE w/o GFCI and now the receptacle is no longer compliant.
Kind of messy. Like I said before, differing requirements for a receptacle based on what gets plugged into it is nuts!