Typically in apartment buildings which levels do they install? I would imagine level 2 correct me if I’m wrong. How many kw typically in apartment buildings do level 2 consume?If you're talking the typical "Level 2" (J1772, regular 208V or 240V AC 2-wire), those can be set up to 80A, with 30A/32A and 40A being common.
For "Level 3" (DC Fast Charge), that's 25 kW - 200kW, with 50kW and 100kW common. But those are nominal output ratings at 500V DC (IIRC), so I expect the corresponding input ratings are higher.
Cheers, Wayne
I think 30A Level 2 would be typical, and Level 3 would be pretty rare for an apartment building. For 30A 208V, 6.24 kW, etc. No losses--Level 2 EVSE is just a slightly smart switch that can tell the EV how much current is available and open and close a contactor.Typically in apartment buildings which levels do they install? I would imagine level 2 correct me if I’m wrong. How many kw typically in apartment buildings do level 2 consume?
Super duper helpful thank you!Also, note that breakers on feeders supplying EVSEs need to be sized for 125% of the EVSE continuous current (with no exception for 100% rated breakers; I think that's an oversight). If you have a 400A 3 phase breaker as your supply, you can only use 320A for EVSEs. Divide by sqrt(3), and that's 184A available per phase (pair of line conductors). So you could do 6 * 3 = (18) 30A EVSEs on that 400A 3 phase breaker.
Cheers, Wayne
I can imagine that insurance companies would have some concern for a bunch of level 3 EV chargers running in the basement garage of an apartment complex… The car batteries get pretty toasty when being charged by L3 chargers.I have never seen nor heard of an apartment building with level 3 DC charging. Always L2 (or just a receptacle). 5 to 7KW is pretty typical for public L2.