bwrams
Member
- Location
- South Carolina
- Occupation
- Engineer
First, sorry for the long post!
I am a novice to hazardous area installations but have been tasked with assisting a team that is evaluating a contractor's design for a C1D2 installation. I've read NEC500, 501, & 504 and ANSI/ISA 12.12.01 but am having difficulty addressing some outstanding questions I have. Before I engage with this contractor and team, I would like to minimize my knowledge deficiencies in this area. The summary of the installation and my outstanding questions are below. If anyone can help answer these or even better, point me toward documentation / standards that would address these topics, I would be grateful.
Control Panel will be installed in a non-hazardous area. Basic panel design is Allen Bradley CompactLogix IO with all 24VDC powered IO (analog and discrete). There are no IS barriers in this panel design. The Power supply and CompactLogix IO are listed as suitable for installation in C1D2 area (but again panel is in the non-hazardous area). The panel design is not distinguishable from any general purpose PLC panel.
The field hardware is a mix of pressure/temperature transmitters, actuated valves, flowmeters, and level switches.
The transmitters are rated C1D1 explosion proof, as well as have IS and nonincendive ratings.
The flowmeters are rated C1D1 explosion proof.
The valves (solenoids and position switches) are rated as C1D2 (not certain if they are listed as nonincendive).
The level switches are rated as C1D2.
The contractor has specified PLTC for most of the connections between the field hardware and the control panel. And they have noted that seals are required.
I have been able to locate control drawings for some of the field hardware and for some, I have only been able to locate manufacture's installation instructions.
My difficulty is determining whether the contractor has provided a design that meets all NEC installation requirements and incorporates the necessary panel design requirements for the associated field hardware (and their corresponding C1D1 or C1D2 ratings). I think it can be further stated that my misunderstandings are rooted in my lack of knowledge with the protection methods (Explosion Proof, IS, nonincendive, etc.) and when they can and cannot be applied.
My questions are as follows (and they are overlapping and probably somewhat redundant/repetitive)
1) If the Field Hardware is rated for C1D2 or C1D1 and installed in a C1D2 area, AND the conduit/cabling meets the requirements of 501.10(A) or 501.10(B)(1)&(2), does the design of the control panel in the non-hazardous area even matter? In other words, the field hardware meets the area rating, the wire/conduit is correctly installed, therefore the control panel is irrelevant?!?
2) Are the Control Drawings to be adhered to for the field hardware even if the conduit/cabling meets 501.10(A) or 501.10(B)(1)&(2)? For example, the pressure transmitter control drawing states for C1D1 installation and connection to a non-hazardous location, an associated equipment (IS barrier?) must be installed between the transmitter and the control equipment and must have certain parameters for Uo, Io, and Po. The control drawing further states the associated equipment (IS barrier) can be eliminated for C1D2 installation but a different set of parameters for Uo, Io, and Po are provided for the Control Equipment the transmitter will be connected to. In other words, even with properly rated field hardware and correct wire/conduit installation, the control panel hardware selection matters?!
3) Since the control panel design uses C1D2 rated IO hardware and 24VDC power supply, is this potentially resulting in a design that adheres to the Control Drawings for the field instruments? I say potentially, because I assume I would need to get control drawings for all field hardware and compare the Uo, Io, and Po ratings to the PLC hardware ratings to confirm?
4) Since the control panel design uses C1D2 rated IO hardware and 24VDC power supply AND the field hardware is rated C1D1 or C1D2, are the Control Drawings irrelevant? Install the wire/conduit to 501.10(A) or 501.10(B)(1)&(2) and call it a day??
TLDR:
Can someone tell me where to find a document / standard / text book that explains control panel and installation design for a non-hazardous area located control panel connected to C1D2 area located instrumentation?
I am a novice to hazardous area installations but have been tasked with assisting a team that is evaluating a contractor's design for a C1D2 installation. I've read NEC500, 501, & 504 and ANSI/ISA 12.12.01 but am having difficulty addressing some outstanding questions I have. Before I engage with this contractor and team, I would like to minimize my knowledge deficiencies in this area. The summary of the installation and my outstanding questions are below. If anyone can help answer these or even better, point me toward documentation / standards that would address these topics, I would be grateful.
Control Panel will be installed in a non-hazardous area. Basic panel design is Allen Bradley CompactLogix IO with all 24VDC powered IO (analog and discrete). There are no IS barriers in this panel design. The Power supply and CompactLogix IO are listed as suitable for installation in C1D2 area (but again panel is in the non-hazardous area). The panel design is not distinguishable from any general purpose PLC panel.
The field hardware is a mix of pressure/temperature transmitters, actuated valves, flowmeters, and level switches.
The transmitters are rated C1D1 explosion proof, as well as have IS and nonincendive ratings.
The flowmeters are rated C1D1 explosion proof.
The valves (solenoids and position switches) are rated as C1D2 (not certain if they are listed as nonincendive).
The level switches are rated as C1D2.
The contractor has specified PLTC for most of the connections between the field hardware and the control panel. And they have noted that seals are required.
I have been able to locate control drawings for some of the field hardware and for some, I have only been able to locate manufacture's installation instructions.
My difficulty is determining whether the contractor has provided a design that meets all NEC installation requirements and incorporates the necessary panel design requirements for the associated field hardware (and their corresponding C1D1 or C1D2 ratings). I think it can be further stated that my misunderstandings are rooted in my lack of knowledge with the protection methods (Explosion Proof, IS, nonincendive, etc.) and when they can and cannot be applied.
My questions are as follows (and they are overlapping and probably somewhat redundant/repetitive)
1) If the Field Hardware is rated for C1D2 or C1D1 and installed in a C1D2 area, AND the conduit/cabling meets the requirements of 501.10(A) or 501.10(B)(1)&(2), does the design of the control panel in the non-hazardous area even matter? In other words, the field hardware meets the area rating, the wire/conduit is correctly installed, therefore the control panel is irrelevant?!?
2) Are the Control Drawings to be adhered to for the field hardware even if the conduit/cabling meets 501.10(A) or 501.10(B)(1)&(2)? For example, the pressure transmitter control drawing states for C1D1 installation and connection to a non-hazardous location, an associated equipment (IS barrier?) must be installed between the transmitter and the control equipment and must have certain parameters for Uo, Io, and Po. The control drawing further states the associated equipment (IS barrier) can be eliminated for C1D2 installation but a different set of parameters for Uo, Io, and Po are provided for the Control Equipment the transmitter will be connected to. In other words, even with properly rated field hardware and correct wire/conduit installation, the control panel hardware selection matters?!
3) Since the control panel design uses C1D2 rated IO hardware and 24VDC power supply, is this potentially resulting in a design that adheres to the Control Drawings for the field instruments? I say potentially, because I assume I would need to get control drawings for all field hardware and compare the Uo, Io, and Po ratings to the PLC hardware ratings to confirm?
4) Since the control panel design uses C1D2 rated IO hardware and 24VDC power supply AND the field hardware is rated C1D1 or C1D2, are the Control Drawings irrelevant? Install the wire/conduit to 501.10(A) or 501.10(B)(1)&(2) and call it a day??
TLDR:
Can someone tell me where to find a document / standard / text book that explains control panel and installation design for a non-hazardous area located control panel connected to C1D2 area located instrumentation?