I got tagged the other day and this made no sense to me. I had 3 bedrooms in a house and the total square footage totaled 493 sq ft for the 3 bedrooms. Here in Washington we are only required to arc fault bedrooms and bedroom closets. I only installed one arc fault circuit. The inspector wrote me up for this..
Where the load is calculated on the basis of volt-amperes per square meter or per square foot, the wiring system up to and including the branch-circuit panelboard(s) shall be provided to serve not less than the calculated load. This load shall be evenly proportioned among multioutlet branch circuits within the panelboard(s). Branch-circuit overcurrent devices and circuits shall be required to be installed only to serve the connected load.
He said I was only allowed 2 bedrooms per arc fault (which is not in the NEC nor in the WAC (Washington administrative code)). He said it is just something that the inspectors came up with on their own. Not sure how I am suppose to know about it then. He then told me that I did not have my circuit loads evenly proportioned. The house total square footage was 1192 sq ft. I had installed three 15 amp lighting circuits for the house and one 15 amp circuit for the garage lights and plugs.
I had read another post a few weeks back that had mentioned that the small appliance circuits had to feed at least 2 counter top plugs. Basically just said that I could have one plug on the counter top on one circuit and then the remaining plugs on the other circuit and still be code compliant. As long as the counter top plugs were served by at least 2 circuits it did not matter how they were split up. Is this true?
Also why does the inspector not have an issue with my garage circuit not having a load similar as the rest of the house? It only has 1 keyless light fixture and 1 gfci plug on it. I don't even understand why it matters if all the circuits in the panel are evenly proportioned. What is the big deal?
Where the load is calculated on the basis of volt-amperes per square meter or per square foot, the wiring system up to and including the branch-circuit panelboard(s) shall be provided to serve not less than the calculated load. This load shall be evenly proportioned among multioutlet branch circuits within the panelboard(s). Branch-circuit overcurrent devices and circuits shall be required to be installed only to serve the connected load.
He said I was only allowed 2 bedrooms per arc fault (which is not in the NEC nor in the WAC (Washington administrative code)). He said it is just something that the inspectors came up with on their own. Not sure how I am suppose to know about it then. He then told me that I did not have my circuit loads evenly proportioned. The house total square footage was 1192 sq ft. I had installed three 15 amp lighting circuits for the house and one 15 amp circuit for the garage lights and plugs.
I had read another post a few weeks back that had mentioned that the small appliance circuits had to feed at least 2 counter top plugs. Basically just said that I could have one plug on the counter top on one circuit and then the remaining plugs on the other circuit and still be code compliant. As long as the counter top plugs were served by at least 2 circuits it did not matter how they were split up. Is this true?
Also why does the inspector not have an issue with my garage circuit not having a load similar as the rest of the house? It only has 1 keyless light fixture and 1 gfci plug on it. I don't even understand why it matters if all the circuits in the panel are evenly proportioned. What is the big deal?