I will try to be as concise as possible (cue the long story)
This summer we started getting minor shocks when using water hose outside (grab the metal handle to turn off, water flowing on us and grass). Testing between the metal spicket and the earth (the soil outside etc) shows 20v. I checked 3 times during the next day, morning 7am- 5volts, 12pm 20volts, 7pm 7volts. Verified the plumbing etc at house is all bonded and shows good continuity there.
I go outside to a random outlet, test between grounding of outlet and the earth (soil) same 20volts.
Utility company comes out around 12pm and turns off my main breaker at house, still reads 20volts.
Utility company removed the meter from the house to disconnect power altogether. The 20volts goes away. I was not present when they did this and do not know if they had truly disconnected everything (neutral etc), or just the supply hot feed.
Utility guy says looks like its from your house has an open or poor connected neutral. I do not know if utility checked to see if their supply side neutral measured 0v to earth or not, I would hope so.
Other property details for full scope:
- nearest neighbor is maybe 1000-1500 ft?
My question(s):
1- If utility service side was to be tested for a bad neutral, wouldnt they need to test this while having a load on the circuit?
2- If my whole house breaker is OFF and it measures to show no power connection through breaker, and company still reads 20volts, to me that would be indicative that its either utility side, the meter itself, or the small span of neutral between service meter and my main breaker, but again with no load no flow, why a reading?
In summary, not sure if I am just not understanding this utility company result fully, or did utility company not completely check on their end? Sorry my electrical background is mostly in electronic controls, industrial equipment etc.
This summer we started getting minor shocks when using water hose outside (grab the metal handle to turn off, water flowing on us and grass). Testing between the metal spicket and the earth (the soil outside etc) shows 20v. I checked 3 times during the next day, morning 7am- 5volts, 12pm 20volts, 7pm 7volts. Verified the plumbing etc at house is all bonded and shows good continuity there.
I go outside to a random outlet, test between grounding of outlet and the earth (soil) same 20volts.
Utility company comes out around 12pm and turns off my main breaker at house, still reads 20volts.
Utility company removed the meter from the house to disconnect power altogether. The 20volts goes away. I was not present when they did this and do not know if they had truly disconnected everything (neutral etc), or just the supply hot feed.
Utility guy says looks like its from your house has an open or poor connected neutral. I do not know if utility checked to see if their supply side neutral measured 0v to earth or not, I would hope so.
Other property details for full scope:
- nearest neighbor is maybe 1000-1500 ft?
My question(s):
1- If utility service side was to be tested for a bad neutral, wouldnt they need to test this while having a load on the circuit?
2- If my whole house breaker is OFF and it measures to show no power connection through breaker, and company still reads 20volts, to me that would be indicative that its either utility side, the meter itself, or the small span of neutral between service meter and my main breaker, but again with no load no flow, why a reading?
In summary, not sure if I am just not understanding this utility company result fully, or did utility company not completely check on their end? Sorry my electrical background is mostly in electronic controls, industrial equipment etc.