Jbudgy
New member
- Location
- Minneapolis MN
For a state exam, when a question doesn't mention termination temperature rating, does one assume 75degree terminations when sizing conductors? or would you apply 110.14c and restrict the ampacity to 60degree column for loads under 100 amps.?
It was previously my belief that we are to assume all terminations are 75 degrees unless told otherwise, although I cannot find that direction in the (MN) dli exam study guide. I understand other state exams might provide different direction, but guessing that its generally a similar practice.
My initial reaction was to not apply 110.14c unless a question says the terminal temperature is not known.
Please correct me if Im wrong.
It was previously my belief that we are to assume all terminations are 75 degrees unless told otherwise, although I cannot find that direction in the (MN) dli exam study guide. I understand other state exams might provide different direction, but guessing that its generally a similar practice.
My initial reaction was to not apply 110.14c unless a question says the terminal temperature is not known.
Please correct me if Im wrong.