Exam help......generator

Status
Not open for further replies.

shelbyvillettcs

New member
A generator connected to the srevice through a transfer switch must have:
A. The generator neutral solidly connected to the service of the neutral
B. Connect the generator neutral to the frame of the generator
C.connect a bonding jumper between the generator ground and generator neutral
D. A separate grounding electrod for the generator
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
There is not enough information to answer the question. See the art 100 definition of seperatly derived system.
 

Denis

Senior Member
Location
50156
D !

just going by memory:

A is wrong because they must not be shared

B is wrong because there are "floating neutral" generators

C is wrong because there are "isolated ground" generators

and now for NEC

250.20 D 250.30 445 art. 700 700.12
 

dezwitinc

Senior Member
Location
Delray Beach, FL
In a scenario of a non seperately derived source, the answer is A.
B is not correct because the neutral must float in non SDS.
C for the same reason.
D for the same reason unless the manufacturer (Guardian/Generac) requires one for lightning "protection".
 

bob

Senior Member
Location
Alabama
shelbyvillettcs said:
A generator connected to the srevice through a transfer switch must have:
A. The generator neutral solidly connected to the service of the neutral
B. Connect the generator neutral to the frame of the generator
C.connect a bonding jumper between the generator ground and generator neutral
D. A separate grounding electrod for the generator
If the transfer switches the neutral, then all are true. B and C are the same thing.

If the transfer switch does not transfer the neutral, then only A is true.
 