I have emailed Mike holt and I am told that I am doing the problem wrong. I believe I am right.
The question asks:
What THHN conductor size is needed for 40A non-continuous load? The ambient temperature is 90F and the terminal size is rated for 60 degrees.
Looking at table 310.15B16 and 60 degree column we find that #8 is rated for 40A. we then use the ambient temperature correction Table and use the insulation rating of the conductors which is 90 degrees and 90 degree F. the correction is .91. We then apply the correction to the 40A we found from table 310.15B16.
So 40A x .91= 36.4A is for #8 THHN at 90F and 60 degree terminals. Mike says that this is not correct, and that #8 Awg is sufficient.
Any thoughts?
The question asks:
What THHN conductor size is needed for 40A non-continuous load? The ambient temperature is 90F and the terminal size is rated for 60 degrees.
Looking at table 310.15B16 and 60 degree column we find that #8 is rated for 40A. we then use the ambient temperature correction Table and use the insulation rating of the conductors which is 90 degrees and 90 degree F. the correction is .91. We then apply the correction to the 40A we found from table 310.15B16.