Someone out there in "forum-Land" please check these answers.
Calculations for a 3 phase motor.
3phase
10 hp
230 v
In the beginning this is all the information I had!
So I calculated the following...
FLC: 28A
EFF 1.495
PF= .668
VA= 11.154kVA
FLA=225A
SF=115
CONDUCTOR SIZE #10
CONDUIT SIZE 3/4'
BRANCH CIRCUIT PROTECTION 70A (INVERSE TIME BREAKER)
FEEDER CONDUCTOR SIZE #10
FEEDER PROTECTION BREAKER 70a
OVERLOAD FUSES 30a
Someone outthere check these calculations (they are from an old training manual I have).
Thank you,
Bob