"A single-family dwelling unit has a net load of 4000VA. A 6kW range will also be included in the design. The dwelling unit is supplied by a 120/240V, three wire, single phase copper feeder of type THW. According to the NEC, what size feeder is required? - AWG3/AWG4/AWG6/AWG8."
The solution references NEC 230.79 - Rating of Service Disconnecting Means and NEC 310.15(B)(7) Single family dwelling services and feeders.
The way this question reads, it sounds like an apartment unit, not a stand alone house. NEC 100 definitions back me up here. (uses term 'unit')
Im thinking that this solution is wrong because the 'feeder' is a feeder and not a service.
the second question is the solution doesnt use the demand factor table of 220.42 for the 4000VA load. Is this because its not specified as a lighting load?