Exam Question: Raintight Service Head

Status
Not open for further replies.

am1954

Member
Location
NY
Occupation
contractor
hey all. i'm trying to understand an exam question. i'm paraphrasing, but i believe it asked if a service head needs to be a) weather tight b) rain tight c) rain proof, etc

230.54(A) states that 'the service head shall be listed for use in wet locations' but i don't see any mention specifically of rain tight, weather proof, etc. when i google the question, there is plenty of mention online that a service head needs to be rain tight, but they all reference 230.54

what am i missing in the interpretation of this question? thanks
p.s. this is based on NEC 2017 for what that's worth
 

am1954

Member
Location
NY
Occupation
contractor
it's a sample question to prep for a test. they don't give the answer though...just let you know what to expect
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Look at the Article 100 definitions for the given answers and see which one fits best to the question.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Do they still allow goosenecks on SE?
Does this answer your question

(A) Service-Entrance Cables. Service-entrance cables shall be
supported by straps or other approved means within 300 mm
(12 in.) of every service head, gooseneck, or connection to a
raceway or enclosure and at intervals not exceeding 750 mm
(30 in.).

(B) Service-Entrance Cables Equipped with Service Head or Gooseneck.
Service-entrance cables shall be equipped with a service head. The service head shall be listed for use in wet locations.
Exception:
Type SE cable shall be permitted to be formed in a gooseneck and taped with a self-sealing weather-resistant thermoplastic.

(C) Service Heads and Goosenecks Above Service-Drop or Overhead Service Attachment.
Service heads on raceways or service-entrance cables and goosenecks in service-entrance cables shall be located above the point of attachment of the service-drop or overhead service conductors to the building or other structure.
Exception:
Where it is impracticable to locate the service head or gooseneck above the point of attachment, the service head or gooseneck location shall be permitted not farther than 600 mm (24 in.) from the point of attachment.
 