Do You Like Ham
Member
- Location
- TX, USA
In the Appendix D, sample calculation D1(a)... Can someone tease apart for me why the neutral calculation is essentially putting 50% of the demand receptacle load on the neutral + 70% of Range and Dryer?
I understand the reference to 220.61 for the 70% reduction.. but since the range/drier are 240V... why do they have any relation to the neutral current calculation?
This is my 'mental model' of the "Service or Feeder" vs. the "Neutral Conductor"... as the sample calculation shows...
Seems to me the worst case for the neutral would be that half the loads in the residence are on, and all on the same phase, while the other half are off... like this.. (the drier/range being irrelevant). what am I misunderstanding?
I understand the reference to 220.61 for the 70% reduction.. but since the range/drier are 240V... why do they have any relation to the neutral current calculation?
This is my 'mental model' of the "Service or Feeder" vs. the "Neutral Conductor"... as the sample calculation shows...
Seems to me the worst case for the neutral would be that half the loads in the residence are on, and all on the same phase, while the other half are off... like this.. (the drier/range being irrelevant). what am I misunderstanding?