Example D4(a) Error?

Status
Not open for further replies.

gray.one

Member
Location
Reston, VA
a139bd6e8bd87e5940246461f07f0473.jpg



Shouldn't the reduction in 220.61(B)(2) be based on the current without the reduction of 220.61(B)(1)?


Sent from my iPhone using Tapatalk
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Not IMO, I think the example is correct. 220.61(A) gives us the calculation for the unbalanced loads for the 120v loads. Then 220.61(B) gets more specific and states that we can take 70% off the neutral current on specific appliance and any neutral current over 200 amps. It does not say either A or B so you do it for both
 