Hello,
With a shortage of modules in my area, we are having a tough time finding modules that abide by all inverter input specifications. There are an abundance of bi-facial modules meeting most requirements except the maximum IMP.
I understand an overvoltage in any scenario can be destructive. However, after little research it appears some inverter MPPTs will throttle, "ignore", or clip excess current. I am not yet convinced.
Say an inverter max IMP is 15 amps and these modules have a IMP of 15.1A. What are the implications here, is IMP a less "strict" max than VMP?
Ultimately, I'd like to find another module if possible for safety and warranty purposes, this is getting tougher to do, have any of you exceeded these values?
This specific case will use a tesla PW3, but the question remains to all inverters.
(I'm aware you can jumper PW3 inputs to increase current capacity, but not all MPPTs and this will not work for larger more complex roof set-ups with the module mentioned earlier)
Thanks
With a shortage of modules in my area, we are having a tough time finding modules that abide by all inverter input specifications. There are an abundance of bi-facial modules meeting most requirements except the maximum IMP.
I understand an overvoltage in any scenario can be destructive. However, after little research it appears some inverter MPPTs will throttle, "ignore", or clip excess current. I am not yet convinced.
Say an inverter max IMP is 15 amps and these modules have a IMP of 15.1A. What are the implications here, is IMP a less "strict" max than VMP?
Ultimately, I'd like to find another module if possible for safety and warranty purposes, this is getting tougher to do, have any of you exceeded these values?
This specific case will use a tesla PW3, but the question remains to all inverters.
(I'm aware you can jumper PW3 inputs to increase current capacity, but not all MPPTs and this will not work for larger more complex roof set-ups with the module mentioned earlier)
Thanks