Forum,
We have a VFD for a 350hp, 480v motor that's connected to a resistance-grounded wye system. The other day our HRG alarms were going off, so we began to troubleshoot. Phase-to-phase and phase-to-ground voltages looked fine, the current was evenly distributed along all three phases, but one thing stood out to me: the GND wire was carrying 4.8 - 5.0A of current. Is this excessive leakage current? I looked for filters and the VFD has a line filter, but not a load one. This is either a Toshiba G9 or an H9, can't remember which one exactly. I was looking through the manual and I think the root cause is the grounding capacitors are not set-up properly for an HRG system. Could this be a root cause? Let me know, thanks