exfrmer primary ocpd

Status
Not open for further replies.

Toros

Senior Member
Location
Tujunga, CA
Hi,
I have a 500 kVA , 3-ph. @ 480/600v dry type transformer ,
if the primary is 400A C.B, what is the current of secondary @ 120/208v ???????

900A @ 120/208V ??????


Thank you
 

kwired

Electron manager
Location
NE Nebraska
I agree with don, you have a 500 kVA coil. If you only have a 400 amp breaker on the primary you will trip it before you ever can deliver 500 kVA for any sustained period of time though. @ 480 volts that 400 amp breaker sort of limits you to only 332.5 kVA.

Not sure what you mean by 480/600 volt primary, unless it has taps for both voltages. I would think that would be sort of rare to have though.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Even with a 600 volt primary, I would be surprised if a 400 amp breaker would hold when you turn the primary on.
 