Since arc fault breakers offer about 30ma of ground fault protection, would that satisfy the manufacturers requirement for GFCI protection for exhaust fans within a shower space?
Why do you have afci in the bathroom? One of the reasons for not requiring AFCI in the baths and kitchen is because of exhaust fans, I believe.
I also agree with Derek.
I'll assume that it's a residential bathroom, how do you get by or meet the requirements of Article 210.8 (A) or if not a residence (B)?
This most be a very usual requirement of a free standing shower...
The lighting circuit in the bathroom is fed from the master bedroom circuit hence AFCI protection.
I dont have my book with me. Please expand on your reference 210.8. This is a residence.
I always avoid that when possible.
In a nutshell, the UL and manufacturer required GFI protection for the exhaust fan in a residential bath or shower space is for protection of personnel, not for protection of the equipment.
The 5 to 6 mA trip of a class A GFI is tied to the heart of a person, that is, most people can't tolerate current levels above this when in the cross section of the heart - the worst case through body fault.
Arc Fault Interrupters that have a GFI component can have trip levels at 60 mA. That's an order of magnitude greater.
Chest muscles constrict and suffocation occurs at 35 mA.
The GE Combination Arc Fault doesn't have a GFI trip.
Arc Fault Interrupters that have a GFI component can have trip levels at 60 mA. That's an order of magnitude greater.[/QUOTE said:is there a AFCI/GFCI combo unit?
Back to OP question, You have to follow manufacturers requirement, almost all exhaust fans that are installed in the shower area require GFCI protection. On a second note, I don't see a problem having a GFCI unit on a lighting circuit that is AFCI protected.
A Bathroom needs a circuit and GCFI for receptacle protection, thus a off shoot off of a Bedroom AFCI suppling a circuit to a bathroom recepacle is a Code violation.
Sorry but you are wrong. If I run a dedicated 20A circuit for the bathroom receptacles, I can supply 10 bathrooms with that circuit as long as it only supplies receptacles. The lighting and exhaust fans can be tapped from any circuit with adequate ampacity.
I'm not wrong, if you need to supply a gfci protection per the manufacture, I said what to do.
I don't know how these simple questions can get so convoluted.