Service is 3000A - GFP main
Existing 600A feed off service to Life safety ATS. This is a 3-pole ATS.
Owner is considering adding a Generator for full bldg backup.
After GFP main in service, bussing would be modified to feed (N) ATS and back into the service to feed rest of the board.
My understanding is due to the GFP main, the (N) ATS should be a SDS with N-G bond and a 4-pole ATS.
However, this generator will also be feeding the existing life safety ATS that is 3-pole.
This is no good, right? Would the existing ATS need to be upgraded to 4-pole as well?