A replacement Lennox brand AC unit and 60-amp fusible pullout disconnect with 45 amp fuses with copper # 8 THHN branch circuit wiring in a whip to the outside AC unit was installed. The feeder to this pullout disconnect is a SE cable with #8 Aluminum wire that runs indoors to the residential electrical panel and is protected by a two pole 50 amp breaker. This feeder and breaker appear to be original house wiring for the previous AC unit.
The AC unit nameplate requires a minimum circuit ampacity of 28 amps and a Maximum Fuse or Circuit Breaker Ampacity of 45 Amps.
Do you think that the wiring and/or overcurrent protection which was original and upstream of the 60-amp fusible pullout disconnect needs to be replaced?
If so what size wire and breaker is needed. Is it the homeowner's or contractor's responsibility?
The home is 20 or more years old.
Thanks.
The AC unit nameplate requires a minimum circuit ampacity of 28 amps and a Maximum Fuse or Circuit Breaker Ampacity of 45 Amps.
Do you think that the wiring and/or overcurrent protection which was original and upstream of the 60-amp fusible pullout disconnect needs to be replaced?
If so what size wire and breaker is needed. Is it the homeowner's or contractor's responsibility?
The home is 20 or more years old.
Thanks.