We have a client who owns a warehouse building with a single 3000A service fed from a pad mounted transfomer. Metering is in the switchboard by way of a utility company metering compartment.
The client is splitting the building into 2 separate tenants and wants to feed the new tenant space with a separately metered service.
Working through the details of this if permitted and requirements.
The existing service would remain as is.
The ‘second’ service would be fed from the same utility transfomer with a new set of service entrance conductors. Feeds would come from this utility transfomer to an outdoor pad mounted metering compartment and feed into the building landing on the new service entrance disconnect at a new location.
Is this permitted by 230.2 provided there is a fire wall between the 2 spaces making each space its own ‘building’ as per the definition of a building.
Is that the only way this would be allowed?
Thanks for any replies!
The client is splitting the building into 2 separate tenants and wants to feed the new tenant space with a separately metered service.
Working through the details of this if permitted and requirements.
The existing service would remain as is.
The ‘second’ service would be fed from the same utility transfomer with a new set of service entrance conductors. Feeds would come from this utility transfomer to an outdoor pad mounted metering compartment and feed into the building landing on the new service entrance disconnect at a new location.
Is this permitted by 230.2 provided there is a fire wall between the 2 spaces making each space its own ‘building’ as per the definition of a building.
Is that the only way this would be allowed?