This is the situation. We are renovating an old gym and the existing exit signs are recessed in the wall at there perspective locations. Can I use the existing housing of the fixture as a junction box to terminate the connections and mount the new exit sign over the old one?
 
This is the situation. We are renovating an old gym and the existing exit signs are recessed in the wall at there perspective locations. Can I use the existing housing of the fixture as a junction box to terminate the connections and mount the new exit sign over the old one?

In the real world I use it but I would make my termination in the new fixture even if I had to re-pull the wire. They could sight 314.29 but it would be a stretch.
 