When performing a service call at a local convenience store I noticed the lever on the disco sw was broken off. The store has a 400a sgl. ph. and 400a 3 ph. grd. delta service. I lifted the door on the 400a sgl. ph. disco and noticed there was no egc run into the store. I checked the other 2 discos for the 3 ph. and same thing. Opened panels inside and confirmed no egc's.
The company has approved the upgrades to bring the services up to date in regards to disco replacement and grounding. My question is that there is a GEC running from each disco into the concrete sidewalk but I cannot see what they are connected to? Should I drive two new rods just in case?