Existing light switches

Captorofsin1

Member
Occupation
Electrical contractor
Hello everybody. Fully wear wear with new construction and remodels that NEC does require that all light switches be grounded.

My question is there anywhere in code that mandates that if I remove and replace a light switch I have to ground it?

Little bit of an embarrassment factor. I've looked and looked and looked and looked and cannot find anything on this subject. Maybe I wasn't looking in the right places 😀.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
If you're talking about having an actual EGC (ground) in the box, then if there is not one there, then you don't have to bring one to it. If there is, then you have to land it on the ground terminal/screw of the switch.
 

Captorofsin1

Member
Occupation
Electrical contractor
Done that before. So if I'm removing and replacing a light switch and it's not grounded but there are grounds twisted together, capped off, and pushed to the back of the box I have to pull off of those grounds, right?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I'm not offering an answer but the grounding switch requirement was put into code when the CMP was bored and was looking for something to waste time and material on. If the existing does not have an EGC personally I wouldn't worry about it.
 

norcal

Senior Member
While I am well aware of what is said about opinions, I am asking about switch replacement with existing grounded metal boxes, would you find & connect the ECG from a existing box installed prior to the requirement to connect a EGC to each switch, with NM cable as the wiring method?
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
I am asking about switch replacement with existing grounded metal boxes, would you find & connect the ECG from a existing box installed prior to the requirement to connect a EGC to each switch, with NM cable as the wiring method?
New switches are self grounding through a mounting screw to the grounded metal box. No additional ground needed.

-Hal
 

letgomywago

Senior Member
Location
Washington state and Oregon coast
Occupation
residential electrician
New switches are self grounding through a mounting screw to the grounded metal box. No additional ground needed.

-Hal
But that only applies if the box is metallic and there's a good chunk of 80s installs with NM boxes and short short grounds.

I happen to know that some people skip those when replacing a switch if it's hard to get at cough cough
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes the switch is required to be grounded. Metal boxes only require the two 6/32 screws to be connected to the box. If the box is plastic then connection to the EGC is required.
 