scrub12
Member
- Location
- Cleveland, OH
- Occupation
- Electrical Engineer
I have a 1600A main breaker. I've compiled load data for the last year to get a peak load. I am adding load to this existing service but want to ensure the breaker is sized appropriately. Utilizing NEC, Article 220.87 states, "The maximum demand at 125% plus the new load does not exceed the ampacity of the feeder or rating of the service." The 1600A breaker is 80% rated. Do I need to add 25% to the new load (Continuous Load) or is it permitted just to utilize 125% of the existing load plus the new connected load at 100%?