WA_Sparky
Electrical Engineer
- Location
- Vancouver, WA, Clark
- Occupation
- Electrical Engineer
I have a coffee shop project that has a 200A service. Utility said there are 6 disconnects already, we cannot upgrade service to 400A and they highly doubt inspector will allow separate service to the building. Im assuming this is because the tenants are not separated by fire wall which would allow another group of disconnects.
Existing load info from utility is only showing 27A at 208/3. All is getting demoed minus existing mech units (60A/3,40A/3), Water heater (30A/2), bathroom circuit, and an unknown 30A/2 circuit.
There is no question that actual installed load will be under panel ampacity but these questions are specifically to ensure load calculations are code compliant.
Trying to determine existing load vs load removed:
If I know the existing mech equipment nameplate rating, do I have to use that as existing load remaining on panel or can I have those circuits 30 day metered?
For unknown circuits, should I consider 80% of the breaker rating as existing load or would it be better to meter each existing circuit to remain?
If the majority of the building is getting demoed, would this be considered "New Restraunt"?
Any possible loop holes or workarounds:
With new loads + 80% of existing loads, demand is 260A.
If demand calcs cannot be manipulated to be below panel amperages, what would be the best option to ensure everything is done by the book.
A. Try and have some loads moved to house panel and attempt to get tenant and building owner to agree on prorated electrical bill.
B. Work with utility to add 1200A/3 disconnect ahead of utility switch gear to get around 6disconnect rule.
C. Permit 90% of equipment installed, 30 day meter to find new "existing load", then install remaining 10% of equipment to keep demand below panel amperage.
D. Try to persuade inspector to allow additional service if existing meter (in existing switch gear) is capped and maxed at 5 disconnects?
Thanks in advance for your input!
Existing load info from utility is only showing 27A at 208/3. All is getting demoed minus existing mech units (60A/3,40A/3), Water heater (30A/2), bathroom circuit, and an unknown 30A/2 circuit.
There is no question that actual installed load will be under panel ampacity but these questions are specifically to ensure load calculations are code compliant.
Trying to determine existing load vs load removed:
If I know the existing mech equipment nameplate rating, do I have to use that as existing load remaining on panel or can I have those circuits 30 day metered?
For unknown circuits, should I consider 80% of the breaker rating as existing load or would it be better to meter each existing circuit to remain?
If the majority of the building is getting demoed, would this be considered "New Restraunt"?
Any possible loop holes or workarounds:
With new loads + 80% of existing loads, demand is 260A.
If demand calcs cannot be manipulated to be below panel amperages, what would be the best option to ensure everything is done by the book.
A. Try and have some loads moved to house panel and attempt to get tenant and building owner to agree on prorated electrical bill.
B. Work with utility to add 1200A/3 disconnect ahead of utility switch gear to get around 6disconnect rule.
C. Permit 90% of equipment installed, 30 day meter to find new "existing load", then install remaining 10% of equipment to keep demand below panel amperage.
D. Try to persuade inspector to allow additional service if existing meter (in existing switch gear) is capped and maxed at 5 disconnects?
Thanks in advance for your input!