hbendillo
Senior Member
- Location
- South carolina
Is there any room for engineering judgment for determining existing loads? My example is this: Panelboard A is to be refed from Panelboard B. The connected loads for both panelboards are known and verified. The total connected load for Panelboard B when the load is transferred exceeds the rating of the Panelboard by 3%. That is if you consider the connected loads at 100% demand.
Panel A feeds VAV boxes with electric heat throughout the facility. Panelboard B mainly feeds air handling units that are strictly motors with no electric heat.
I am confident that the diversity in the load will allow the addition of the load to Panelboard B. However, the NEC gives no recourse other than NEC 220.87.
Is this strictly an AHJ call or can I use my own engineering judgment?
Panel A feeds VAV boxes with electric heat throughout the facility. Panelboard B mainly feeds air handling units that are strictly motors with no electric heat.
I am confident that the diversity in the load will allow the addition of the load to Panelboard B. However, the NEC gives no recourse other than NEC 220.87.
Is this strictly an AHJ call or can I use my own engineering judgment?