Hello Members,
We working on a project in San Jose, CA for replacement of old motor-pumps fed from a legacy (Westinghouse) MCC.
Provide New connections for new 125 HP, 460V,3-ph motor-pumps. The existing MCC (480V,3-ph) is > 400' away.
The client wants new ABB ACH550 VFD's (w/ C.B) to control the motor-pumps.
The VFD's cannot be retrofitted into the legacy MCC .
Plan : 400A-3P C.B in (E)MCC* - > Feeder/s (~60') - > VFD -> Feeder/s up-to (E)MCC -> Run new conductors from the VFD (>400') through the (E)MCC to go through the existing U.G conduits to connect to the new motor-pumps (thru Disconnect).
* After demo out the old starter disconnects..
(needless to say the client is not keen on any expensive/elaborate construction).
Questions :
1. Can we use (E)MCC to run conductors through it into existing conduit/s ? What are the Code considerations in this kind of install ?
2. If we go with a VFD (w/fused-disconnect) - Can the 400A-3P C.B at the MCC provide the protection for the downstream ?
OR, a fused-disconnect switch at MCC and the VFD (w/C.B) will be a better option ?
3. Any other considerations or code issues that can be foreseen cropping up during this installation ?
Thank you for your time & effort.
Best Regards
We working on a project in San Jose, CA for replacement of old motor-pumps fed from a legacy (Westinghouse) MCC.
Provide New connections for new 125 HP, 460V,3-ph motor-pumps. The existing MCC (480V,3-ph) is > 400' away.
The client wants new ABB ACH550 VFD's (w/ C.B) to control the motor-pumps.
The VFD's cannot be retrofitted into the legacy MCC .
Plan : 400A-3P C.B in (E)MCC* - > Feeder/s (~60') - > VFD -> Feeder/s up-to (E)MCC -> Run new conductors from the VFD (>400') through the (E)MCC to go through the existing U.G conduits to connect to the new motor-pumps (thru Disconnect).
* After demo out the old starter disconnects..
(needless to say the client is not keen on any expensive/elaborate construction).
Questions :
1. Can we use (E)MCC to run conductors through it into existing conduit/s ? What are the Code considerations in this kind of install ?
2. If we go with a VFD (w/fused-disconnect) - Can the 400A-3P C.B at the MCC provide the protection for the downstream ?
OR, a fused-disconnect switch at MCC and the VFD (w/C.B) will be a better option ?
3. Any other considerations or code issues that can be foreseen cropping up during this installation ?
Thank you for your time & effort.
Best Regards