I have a client with an existing 5 meter center ( 1-2 vertically stacked meters, 1-3 vertical stacked meter ).
They need to replace the meter center due to corrosion. Can I place a 400 A main disconnect on to a gutter to feed the meter center (load calcs work)
and do a 1 for 1 replacement with an identical meter center and still be NEC 2020 Code compliant ?
I will need 22k breakers or can also use RK1 fuses 400 A fuses. ( 240v 1 ph 400 A total service ) .
For surge protection, if a panel is full can I ( T ) the load side of an appropriate breaker or do I need to wafer 4 breakers of existing panel and use a type
2 surge protector ?
Thanx, DHSVCS