malachi constant
Senior Member
- Location
- Minneapolis
We're doing the engineering on an existing indoor pool where the deck is getting replaced. We expect the existing "perimeter surfaces bonding conductor" to be buried bare in the mudding just below the tile, and so are putting in our documents that the contractor shall replace this.
We wondered if while we're touching that, maybe an inspector will require us to bring more of the pool grounding system up to code, so took a look at the existing 1970s-era documents to see what they probably have installed. We found a pool grounding detail with a note that reads, "Grounding conductor this area must be aluminum, copper is not permitted due to possible reaction between the aluminum pool shell and the copper." This is at odds with what the NEC allows - 680.26(B) states copper shall bond parts together.
Any thoughts on how to handle this? My inclination is to simply replace the aluminum that is likely to get nicked with copper, and join them with rated splices. We would also call out for the contractor to both visually inspect and test the grounding system. However if there is a serious issue with copper being in the vicinity of an aluminum pool shell we would need to rethink that, probably get the inspector involved sooner than we typically would.
Thanks!
We wondered if while we're touching that, maybe an inspector will require us to bring more of the pool grounding system up to code, so took a look at the existing 1970s-era documents to see what they probably have installed. We found a pool grounding detail with a note that reads, "Grounding conductor this area must be aluminum, copper is not permitted due to possible reaction between the aluminum pool shell and the copper." This is at odds with what the NEC allows - 680.26(B) states copper shall bond parts together.
Any thoughts on how to handle this? My inclination is to simply replace the aluminum that is likely to get nicked with copper, and join them with rated splices. We would also call out for the contractor to both visually inspect and test the grounding system. However if there is a serious issue with copper being in the vicinity of an aluminum pool shell we would need to rethink that, probably get the inspector involved sooner than we typically would.
Thanks!