Kaia8172006
Member
- Location
- Minnesota
- Occupation
- GC
Commercial remodel: we are adding a room in a back warehouse and there is a raceway with existing wires running from panel to a junction box 30’ away that is 10ft off the floor strapped to wall. Conduit runs out of panel box up 20’ and is strapped to corrugated ceiling continues for 30’ and then comes down on wall to junction box. We planned to tap into the junction box to feed lights for new room. The circuit feeding the junction box is not being used. Electrical inspector said we can’t tap into the junction box because the conduit is strapped to the ceiling and needs to be moved 3” down from ceiling or to run a new raceway and pull new wires. I always thought if raceway was existing and wire are existing you can use the box as long as you stay at least 3” down from the box. As junction box is 10ft down from ceiling so we would be way below. Does anyone know the code about conduit and strapping and wether we can use the junction box? I don’t think electrical inspector is interpreting the code correctly. Thanks