150amp service. Range breaker 50amp rated 75c. Aluminum cable rated 90c. Range receptacle rated 75c.
I think the installer was correct to use the wire at 75c -50amp rating instead of 60c- 40amp because panel, breaker and receptacle are rated for 75c.
Your input always appreciated
150amp service. Range breaker 50amp rated 75c. Aluminum cable rated 90c. Range receptacle rated 75c.
I think the installer was correct to use the wire at 75c -50amp rating instead of 60c- 40amp because panel, breaker and receptacle are rated for 75c.