Exit sign

Status
Not open for further replies.

mricks

Member
Does anyone know if it is against code to splice inside of an LED exit sign? If yes or no could you please provide the code stating so.

Thanks,
 
I assume by splicing you mean splicing another ckt or continuing ckt through, as opposed to in the outlet box ? if the fixture is designed and listed for splicing then its ok, otherwise not 410.11
 
Actually we are not splicing to extend a circuit. We need to terminate these signs but dont know if we need a j-box on the outside of the light or if this connection can be made inside the sign.
 
mricks said:
Actually we are not splicing to extend a circuit. We need to terminate these signs but dont know if we need a j-box on the outside of the light or if this connection can be made inside the sign.

I hope you have mounted the signage to a box? If yes, you terminate in the j box section provided above and incorporated within the signage housing.
 
Just about every exit, egress, or combo that I've installed used a box. However, I almost always add pigtails so I can mount the housing and make the last connection. Many now come with Wago-type connectors, and they're made up inside the unit.

I'd say that a unit housing must have a KO or other method to terminate a wiring method in order to not need a box behind or above it.
 
The exit lights I use have a half inch knockout, as well as a whole bunch of hole configurations for mounting on different boxes. If I'm mounting it on a wall, I just use the ko and run MC cable directly into the fixture.
 